Engineering ToolBox > Acoustic Calculation of Ventilation Systems
Acoustic calculation of a ventilation system should follow a procedure similar to:
Determine the sound pressure level criteria. This table scan be used but should be checked against domestic rules.
In the example below Noise Rating - NR30 - is used as the criterion where the NR-values are entered in line 1.
The sound pressure levels- Lp - are converted to sound power level- Lw - at the terminals. The acoustic characteristics of the room as well as the number and location of the terminals must be considered.
a) Determine the acoustic characteristics of the room. In the example an average sound absorption for the room is used.
b) Determine whether the receiver are in the direct or reverberant field. In the example the listener is aprox. 1.5 m from the terminal.
c) Find the rooms absorption characteristics. In the example the absorption for the walls, ceiling, floor, persons, curtains and their areas, is calculated to 30 m2 sabin. According a) and c) the attenuation is 8 dB.
d) Determine how many terminals the listener are influenced by. Note! Remember to include supply and return fans. In the example the listener are influenced by two terminals. From c) we subtract 3 dB.
The attenuation from the terminal to the room is 5 dB. The values are entered in the example below.
In the example the duct dimension is 250 mm. Attenuation due to end reflection is entered below.
Calculate the attenuation in unlined and lined ducts. Note that the table and diagrams list the attenuation indB/m.
Calculate the attenuation in the elbows.
Determine the allowance for split - branch to terminals.
Determine the allowance for split - main duct to branch.
Enter the manufacturer's sound power data or calculate the fan sound power.
Enter safety factors - recommended to -3 dB.
The silencer must be selected to provide the necessary attenuation. For this the manufacturer's data should be used.
| Procedure | Octave band center frequency, Hz | |||||||
| 63 | 125 | 250 | 500 | 1000 | 2000 | 4000 | 8000 | |
| 1. Sound pressure level criterion | 59 | 48 | 40 | 34 | 30 | 27 | 25 | 23 |
| 2. Room and terminal effect | 5 | 5 | 5 | 5 | 5 | 5 | 5 | 5 |
| 3. Allowance for end reflection | 12 | 8 | 4 | 1 | 0 | 0 | 0 | 0 |
| 4. Ductwork attenuation, terminal to checkpoint | 17 | 17 | 9 | 5 | 5 | 5 | 5 | 5 |
| 5. Elbow attenuation, terminal to checkpoint | 0 | 0 | 7 | 15 | 25 | 25 | 19 | 15 |
| 6. Power-level split, branch to terminals | 6 | 6 | 6 | 6 | 6 | 6 | 6 | 6 |
| 7. Power-level split, main duct to branch duct | 10 | 10 | 10 | 10 | 10 | 10 | 10 | 10 |
| Totals | 109 | 91 | 78 | 73 | 78 | 75 | 67 | 61 |
| 8. Sound power level of fan - Lw | 102 | 99 | 98 | 98 | 97 | 95 | 86 | 81 |
| 9. Safety factors | 3 | 3 | 3 | 3 | 3 | 3 | 3 | 3 |
| Total sound power level of fan - Lw | 105 | 102 | 101 | 101 | 100 | 98 | 89 | 84 |
| 10. Silencer requirements | 0 | 8 | 20 | 25 | 19 | 20 | 19 | 20 |