Engineering ToolBox > Air Curtains and Air Screens
Air curtains and air screens blows heated air (or cooled air in summertime) across door openings and reduces the ingress of cold air (or hot air in summertime) from the outside due to wind forces and natural draught through the building.
The forces acting on an opening like a door into a warehouse, mall or similar can be summarized to
The natural draught depends on the height of the building (open inside height) and the temperature difference between outside and inside air. The differential pressure due to natural draught in a building doorway with inside temperature 20oC, outside temperature 0oC and building height 10 m is approximately 10 Pa. With -20oC and a building height of 20 m the natural draught pressure is close to 40 Pa.
The wind force acting on an opening in the wall is proportional with mass times the velocity squared. The pressure at 10 m/s (36 km/h, 22 mph, Beaufort Fresh Breeze ) is 60 Pa.
By direction the airflow with an angel out of the door it is possible to resist the natural draught and wind forces. The strength of an air curtain follows the formula
An Air Curtain that blows at twice the speed has four times the resisting power at the same air volume.
In general the discharge velocities should not exceed
Note that maximum discharge velocity depends on the location of the discharge nozzle. The discharge velocity must increase as the air curtin unit is mounted higher so the air stream will hit the floor with the required velocity that stabilizes the air stream.
For ware houses, shopping malls and similar buildings with openings up to 2.5 m the velocity should not exceed 5 - 9 m/s. For industrial buildings the velocity can be exceeded to 35 - 40 m/s.
The quantities required depends on many variables and an exact calculation may often be hard to perform. Values of 2,000 - 5,000 m3/h air per m2 door opening are common.
Note! Exposed applications with
may even double the values.
The strength of an air curtain is the maximum potential differential pressure it can resist. The potential pressure resistance generated by an airflow through an inlet opening can be expressed as
Δp = 2.2 q2 sin(α) / b H3/4 (1)
Δp = potential differential pressure over the opening in the wall (Pa, N/m2)
q = air flow through discharge nozzle (m3/s per meter opening width in wall)
α = airflow angle (normally between 20 - 30o)
b = depth of discharge nozzle (m)
H = height of door opening (m)
The average air velocity through the discharge nozzle can be expressed as
v = q / b (2)
v = average velocity (m/s)
Note! The average air velocity is per meter opening width in wall. The velocity should not exceed the values mentioned above.
The calculator below can be used to estimate the strength of an air curtain by calculating the pressure difference and velocity in the air flow. Replace the default values with the actual values.
The differential pressure shall compensate the differential pressure caused by natural draught and wind velocity.
The height of an entrance opening in to a mall is 2.5 m. The depth of the inlet is 1 m. The air flow angle through the inlet is 25 degrees and the air flow per meter width of the opening is 8 m3/s.
The force against natural draught and wind forces can be calculated with (1) as
Δp = 2.2 82 sin(25) / 1 2.53/4
= 29.9 Pa
The velocity through the inlet can be calculated with (2) as
v = 8 / 1 = 8 m/s
Since the forces compensated with air curtains constantly varies with outside temperatures and wind velocities, it may be necessary with some control devices modulating air flow angles and air flow volumes.
A control of the modulation can be achieved with one or more temperature transmitters located as shown in the figure above.
The air screen discharge temperature should be kept within certain limits. For winter conditions