Engineering ToolBox > Air Heating Systems
It is often convenient to heat buildings with air. Air heating systems may be cost effective if they can be made simple or if they can be combined with ventilation systems. But be aware that due to the low specific heat capacity of air, the use of air for heating purposes is very limited. Large heat loads requires large volumes of air with huge oversized ducts and fans as results. Transporting huge volumes of air also requires a lot of energy.
Required air volume in an air heating system can be calculated as
L = Q / (cp ρ (th - tr)) (1)
L = air volume (m3/s)
Q = heat loss from the building (kW)
cp = specific heat capacity air - 1.005 (kJ/kgoC)
ρ = density of air - 1.2 (kg/m3)
th = heating air temperature (oC)
tr = room temperature (oC)
As a rule of thumb the heating supply temperature should be in the range 40-50oC. The air flow should be in the range 1-3 times the room volume.
(1) expressed in imperial units:
L = Q / (1.08 (th - tr)) (2)
Q = heat (btu/hr)
L = air volume (cfm)
th = heating air temperature (oF)
tr = room temperature (oF)
The diagrams below can be used to estimate heat required to rise temperature in air flows.
A building with a large room with heat loss 20 kW is heated with air with maximum temperature 50oC. The room temperature is 20oC. The required air volume can be calculated as
L = 20 / (1.005 1.2 (50 - 20))
= 0.55 m3/s