Engineering ToolBox > Condensate Generation in Cold Steam Pipes - Imperial Units
The diagram and table below can be used as a roughly estimate of the warm-up condensate load generated when the steam system is heated up.
| Warm Up-Load (lb/100 ft) | |||||||||
| Steam Gauge Pressure (psi) | Pipe Size (inch) | ||||||||
| 2 | 2 1/2 | 3 | 4 | 5 | 6 | 8 | 10 | 12 | |
| 0 | 6.2 | 9.7 | 12.8 | 18.2 | 24.6 | 31.9 | 48 | 68 | 90 |
| 5 | 6.9 | 11 | 14.4 | 20.4 | 27.7 | 35.9 | 53 | 77 | 101 |
| 10 | 7.5 | 11.8 | 15.5 | 22 | 29.9 | 38.8 | 58 | 83 | 109 |
| 20 | 8.4 | 13.4 | 17.5 | 24.9 | 33.8 | 44 | 66 | 93 | 124 |
| 40 | 9.9 | 15.8 | 20.6 | 29.3 | 39.7 | 52 | 78 | 110 | 145 |
| 60 | 11 | 17.5 | 22.9 | 32.6 | 44 | 57 | 86 | 122 | 162 |
| 80 | 12 | 19 | 24.9 | 35.3 | 48 | 62 | 93 | 132 | 175 |
| 100 | 12.8 | 20.3 | 26.9 | 37.8 | 51 | 67 | 100 | 142 | 188 |
| 125 | 13.7 | 21.7 | 28.4 | 40 | 55 | 71 | 107 | 152 | 200 |
| 150 | 14.5 | 23 | 30 | 43 | 58 | 75 | 113 | 160 | 212 |
| 175 | 15.3 | 24.2 | 31.7 | 45 | 61 | 79 | 119 | 169 | 224 |
| 200 | 16 | 25.3 | 33.1 | 47 | 64 | 83 | 125 | 177 | 234 |
| 250 | 17.2 | 27.3 | 35.8 | 51 | 69 | 89 | 134 | 191 | 252 |
| 300 | 25 | 38.3 | 51 | 75 | 104 | 143 | 217 | 322 | 443 |
| 400 | 27.8 | 43 | 57 | 83 | 116 | 159 | 241 | 358 | 493 |
| 500 | 30.2 | 46 | 62 | 91 | 126 | 173 | 262 | 389 | 535 |
| 600 | 32.7 | 50 | 67 | 98 | 136 | 187 | 284 | 421 | 579 |
| 800 | 38 | 58 | 77 | 113 | 203 | 274 | 455 | 670 | 943 |
| 1000 | 45 | 64 | 86 | 126 | 227 | 305 | 508 | 748 | 1052 |
| 1200 | 52 | 72 | 96 | 140 | 253 | 340 | 566 | 833 | 1172 |
| 1400 | 62 | 79 | 106 | 155 | 280 | 376 | 626 | 922 | 1297 |
| 1600 | 71 | 87 | 117 | 171 | 309 | 415 | 62 | 1018 | 1432 |
| 1750 | 78 | 94 | 126 | 184 | 333 | 448 | 746 | 1098 | 1544 |
| 1800 | 80 | 97 | 129 | 189 | 341 | 459 | 764 | 1125 | 1584 |
This table is based on an ambient temperature of 70oF. For an ambient temperature of 0oF, the values should be increased with 15% at 1800 psi and up to 50% at 0 psi.
If you prefer SI units - go here!