Engineering ToolBox > Insulated Steam Pipes - Condensate Load Generated
The diagram and table below can be used to roughly estimates of the condensate load generated in insulated steam pipes at different pressures and sizes.
| Condensate Load (lb/h per 100 ft) | ||||||||||
| Steam Pressure (psi) | Pipe Size (inch) | |||||||||
| 2 | 2 1/2 | 3 | 4 | 5 | 6 | 8 | 10 | 12 | 14 | |
| 10 | 6 | 7 | 9 | 11 | 13 | 16 | 20 | 24 | 29 | 32 |
| 30 | 8 | 9 | 11 | 14 | 17 | 20 | 26 | 32 | 38 | 42 |
| 60 | 10 | 12 | 14 | 18 | 24 | 27 | 33 | 41 | 49 | 54 |
| 100 | 12 | 15 | 18 | 22 | 28 | 33 | 41 | 51 | 61 | 67 |
| 125 | 13 | 16 | 20 | 24 | 30 | 36 | 45 | 56 | 66 | 73 |
| 175 | 16 | 19 | 23 | 26 | 33 | 38 | 53 | 66 | 78 | 86 |
| 250 | 18 | 22 | 27 | 34 | 42 | 50 | 62 | 77 | 92 | 101 |
| 300 | 20 | 25 | 30 | 37 | 46 | 54 | 68 | 85 | 101 | 111 |
| 400 | 23 | 28 | 34 | 43 | 53 | 63 | 80 | 99 | 118 | 130 |
| 500 | 27 | 33 | 39 | 49 | 61 | 73 | 91 | 114 | 135 | 148 |
| 600 | 30 | 37 | 44 | 55 | 68 | 82 | 103 | 128 | 152 | 167 |
| 800 | 36 | 44 | 53 | 69 | 85 | 101 | 131 | 164 | 194 | 214 |
| 1000 | 43 | 52 | 63 | 82 | 101 | 120 | 156 | 195 | 231 | 254 |
| 1200 | 51 | 62 | 75 | 97 | 119 | 142 | 185 | 230 | 274 | 301 |
| 1400 | 60 | 73 | 89 | 114 | 141 | 168 | 219 | 273 | 324 | 356 |
| 1600 | 69 | 85 | 103 | 132 | 163 | 195 | 253 | 315 | 375 | 412 |
| 1750 | 76 | 93 | 113 | 145 | 179 | 213 | 278 | 346 | 411 | 452 |
| 1800 | 79 | 96 | 117 | 150 | 185 | 221 | 288 | 358 | 425 | 467 |
The condensate load calculations are based on a surrounding temperature 70oF and 80% efficient insulation. For temperatures at 0oF the loads should be added approximately 50%.