Engineering ToolBox > Cooling and Heating Equations
The sensible heat in a heating or cooling process of air can be expressed as
hs = 1.08 q dt (1)
hs = sensible heat (btu/hr)
q = air volume flow (cfm, cubic feet per minute)
dt = temperature difference (oF)
The latent heat due to moisture in the air can be expressed as:
hl = 0.68 q dwgr (2)
or
hl = 4,840 q dwlb (3)
hl= latent heat (btu/hr)
dwgr = humidity ratio difference (gram water/lb dry air)
dwlb = humidity ratio difference (lb water/lb dry air)
Total heat due to both temperature and moisture can be expressed as:
ht = 4.5 q dh (4)
ht= total heat (btu/hr)
dh = enthalpy difference (btu/lb dry air)
Total heat can also be expressed as:
ht = hs + hl
= 1.08 q dt + 0.68 q dwgr (4)
An air flow of one cfm is heated from 32 to 52oF. Using (1) the sensible heat added to the air can be expressed as:
hs = 1.08 1(cfm) (52 - 32)(oF)
= 21.6 (btu/hr)