Engineering ToolBox > Copper Tubes to BS (British Standard) 2871 - Dimensions and Working Pressures
Metric Sizes of copper tubes to BS (British Standard) 2871:1972
The copper used in the manufacture of tubes is phosphorus deoxidized copper Cu-DHP defined by British Standard BS. 6017: 1981. This also corresponds to the ISO denomination Cu-DHP.
The minimum copper content is 99.85% and the residual phosphorus content is between 0.013 and 0.050%. This deoxidized copper is not affected by reducing atmospheres and consequently is well suited to welding and brazing. The density of copper is 8.9 g/cm3. its melting point is 1083 0C and its coefficient of linear expansion is 16.8 x 10-6 per 0C (between 20oC and 100oC).
(mm)
Outside Diameter
(mm)
Table X
Half hard light gauge tube
Table Y
Half hard an annealed tube
Table Z
Hard drawn thin wall tube
Thickness
(mm)
Maximum Working Pressure
(N/mm2)
Thickness
(mm)
(N/mm2)
Thickness
(mm)
(N/mm2)
6 6 0.6 13.3 0.8 14.4 0.5 11.3
8 8 0.6 9.7 0.8 10.5 0.5 9.8
10 10 0.6 7.7 0.8 8.2 0.5 7.8
12 12 0.6 6.3 0.8 6.7 0.5 6.4
15 15 0.7 5.8 1 6.7 0.5 5
18 18 0.8 5.6 1 5.5 0.6 5
22 22 0.9 5.1 1.2 5.7 0.6 4.1
28 28 0.9 4 1.2 4.2 0.6 3.2
35 35 1.2 4.2 1.5 4.1 0.7 3
42 42 1.2 3.5 1.5 3.4 0.8 2.8
54 54 1.2 2.7 2 3.6 0.9 2.5
67 67 1.2 2 2 2.8 1 2
76.1 76.2 1.5 2.4 2 2.5 1.2 1.9
108 108.1 1.5 1.7 2.5 2.2 1.2 1.7
133 133.4 1.5 1.4 1.5 1.6
159 159.4 2 1.5 1.5 1.5
