Maximum Drainage Fixture Unit Loads for sanitary piping
The maximum permissible Drainage Fixture Unit (DFU) loads for sanitary piping can be estimated with the table below.
Maximum Drainage Fixture Units - Stacks and Horizontal Fixture Branches
Maximum Drainage Fixture Units (DFU)
Pipe Size Horizontal fixture branch Stacks less than 3 stories in height Stacks more than 3 stories high
NPS
(inches)
DN
(mm)
Total for stack Total for one story
1 1/20) 40 3 4 8 2
20) 50 6 10 24 6
2 1/20) 65 12 20 42 9
3 80 201) 481) 722) 201)
4 100 160 240 500 90
5 125 360 540 1100 200
6 150 620 960 1900 350
0) No water closet permitted
1) Maximum two water closets
2) Maximum six water closets
Maximum Drainage Fixture Units - Building Drains and Building Drain Branches from Stacks
Pipe Size Slope in/ft (cm/m)
NPS
(inches)
DN
(mm)
1/4 (2.1) 1/2 (4.2)
20) 50 21 26
2 1/20) 65 24 31
3 80 421) 501)
4 100 216 250
5 125 480 575
6 150 840 1000