Engineering ToolBox > Torques in Electrical Motors
There are some common torques used to describe and classify electrical motors
Torque is the turning force through a radius and the units is rated in - N.m - in the SI-system and in - lb.ft - in the imperial system.
The torque developed by a synchronous induction motors varies with the speed of the motor when its accelerate from full stop or zero speed, to maximum operating speed.
electric motor current torque curves
Locked Rotor or Starting Torque
The Locked Rotor Torque or Starting Torque is the torque the electrical motor develop when its starts at rest or zero speed.
A high Starting Torque is more important for application or machines hard to start - as positive displacement pumps, cranes etc. A lower Starting Torque can be accepted in applications as centrifugal fans or pumps where the start load is low or close to zero.
Pull-up Torque
The Pull-up Torque is the minimum torque developed by the electrical motor when it runs from zero to full-load speed (before it reaches the break-down torque point)
When the motor starts and begins to accelerate the torque in general decrease until it reach a low point at a certain speed - the pull-up torque - before the torque increases until it reach the highest torque at a higher speed - the break-down torque - point.
The pull-up torque may be critical for applications that needs power to go through some temporary barriers achieving the working conditions.
Break-down Torque
The Break-down Torque is the highest torque available before the torque decreases when the machine continues to accelerate to the working conditions.
Full-load Torque or Braking Torque
The Full-load Torque is the torque required to produce the rated power of the electrical motor at full-load speed.
In imperial units the Full-load Torque can be expressed as:
Tfl = Php 5,252 / ωmax (1)
Tfl = full-load torque (lb.ft)
Php = horsepower
ωmax = maximum shaft rotational speed (rev/min, rpm)
Example - The Braking Torque
The torque of a 60 hp motor rotating at 1725 rpm can be expressed as:
Tfl = 60 (hp) 5,252 / 1725 (rpm)
    = 182.7 lb.ft
NEMA Design
NEMA (National Electrical Manufacturers Association) have classified electrical motors in four different NEMA designs where torques and starting-load inertia are important criterions.
IEC/NEMA Standard Torques
Power (hp) 2 Pole 4 Pole
Locked Rotor Torque Pull Up Torque Break Down Torque Locked Rotor Torque Pull Up Torque Break Down Torque
3 170/160 110/110 200/230 180/215 120/150 200/250
5 160/150 110/105 200/215 170/185 120/130 200/225
7.5 150/140 100/100 200/200 160/175 110/120 200/215
10 150/135 100/100 200/200 160/165 110/115 200/200
15 - 20 140/130 100/100 200/200 150/150 110/105 200/200
Reduced Voltage Soft Starters
Reduced Voltage Soft Starters are used to limit the starting current and reducing the Locked Rotor Torque or Starting Torque and are common in applications which is hard to start or must be handled with care - as positive displacement pumps, cranes, elevators and similar.