Engineering ToolBox > Enthalpy of Moist and Humid Air
The enthalpy of moist and humid air consist of sensible heat and latent heat. The enthalpy is important for calculating cooling and heating processes
Moist air is a mixture of dry air and water vapor. In atmospheric air, water vapor content varies from 0 to 3% by mass. The enthalpy of moist and humid air includes the
Specific enthalpy - h - (kJ/kg) of moist air is defined as the total enthalpy of the dry air and the water vapor mixture per kg of moist air.
Specific Enthalpy of Moist Air
Specific enthalpy of moist air can be expressed as:
h = ha + x hw (1)
h = specific enthalpy of moist air (kJ/kg)
ha = specific enthalpy of dry air (kJ/kg)
x = humidity ratio (kg/kg)
hw = specific enthalpy of water vapor (kJ/kg)
Specific Enthalpy of Dry Air - Sensible Heat
Assuming constant pressure conditions the specific enthalpy of dry air can be expressed as:
ha = cpa t (2)
cpa = specific heat capacity of air at constant pressure (kJ/kg.oC, kWs/kg.K)
t = air temperature (oC)
For air temperatures between -100oC and 100oC the specific heat capacity can be set to
cpa = 1.006 (kJ/kgoC)
Note! that the enthalpy is 0 at 0oC. This is of course not correct according the enthalpy definition in the thermodynamics, but for practical purposes in air psychrometrics it do because our interest is the enthalpy difference.
Specific Enthalpy of Water Vapor - Latent Heat
Assuming constant pressure conditions the specific enthalpy of water vapor can be expressed as:
hw = cpw t + hwe (3)
cpw = specific heat capacity of water vapor at constant pressure (kJ/kg.oC, kWs/kg.K)
t = water vapor temperature (oC)
hwe = evaporation heat of water at 0oC (kJ/kg)
For water vapor the specific heat capacity can be set to
cpw = 1.84 (kJ/kg.oC)
The evaporation heat can be set to
hwe = 2,502 (kJ/kg)
Using (2) and (3), (1) can be modified to
h = cpa t + x [cpw t + hwe] (1b)
or
h = 1.006 (kJ/kg.oC) t + x [1.84 (kJ/kg.oC) t + 2,502 (kJ/kg)] (1c)
Example - Enthalpy in Moist Air
The enthalpy of humid air at 25oC with specific moisture content x = 0.0203 kg/kg, can be calculated as:
h = 1.006 (kJ/kg.oC) 25oC + 0.0203 (kg/kg) [1.84 (kJ/kg.oC) 25oC + 2,502 (kJ/kg)]
= 25.15 (kJ/kg) + 0.93 (kJ/kg) + 50.79 (kJ/kg)
= 76.87 (kJ/kg)
Note! The latent heat due to evaporation of water is the major part of the enthalpy. The sensible heat due to heating evaporated water vapor can almost be neglected.
Enthalpy of Moist Air containing Water - Fog
If the air contains more water than limited by saturation, some of the water exists as droplets - as fog. The enthalpy of moist air with fog can be expressed as:
h = cpa t + xs [cpw t + hwe] + (x - xs) cw t (2)
xs = humidity ratio at saturation (kg/kg)
cw = 4.19 - specific heat capacity of water (kJ/kg.oC)
Enthalpy of Moist Air containing Ice or Snow
If the air contains water as ice or snow, the enthalpy of air can be expressed as:
h = cpa t + xs [cpw t + hwe] + (x - xs) ci t - (x - xs) him (3)
ci = 2.05 - specific heat capacity of ice (kJ/kg.oC)
him= 335 - melting heat of ice (kJ/kg)