Engineering ToolBox > Fan Inlet - Suction Pressure and Air Density
High suction pressure at the fan inlet decreases the density of air and should always be corrected for proper fan selection
If inlet suction pressures exceeds 270 mm W.G (10 in W.G) the change in air density should be compensated by increasing the suction pressures with a correction factor:
Suction Pressure (Water Gauge) Pressure Correction Factor
- f -
mm in
-135 -5 1.01
-200 -7.5 1.02
-270 -10 1.03
-380 -14 1.04
-490 -18 1.05
-600 -22 1.06
For suction pressures below 270 mm W.G (10 in W.G) the correction is normally neglected.
Corrected suction pressure can be expressed as:
Psc = Ps f (1)
Psc = corrected suction pressure (mm W.G., in W.G)
f = correction factor
Ps = design (and measured) suction pressure (mm W.G., in W.G)
Example - Correcting Suction Pressure
Design or measured suction pressure Ps = -380 mm W.G. (-14 in W.G). Correction factor from table above 1.04. For proper fan selection the suction pressure should be corrected to
Psc = -380 1.04 (mm W.G.) = -395 (mm W.G.)