Engineering ToolBox > Flow Coefficient - Cv - Formulas for Liquids, Steam and Gases
The flow coefficient - Cv - let us compare flow capacities of valves at different sizes, types and manufacturers. The flow coefficient is in general determined experimentally and express the flow capacity in imperial units - GPM (US gallons per minute) of water that a valve will pass for a pressure drop of 1 lb/in2 (psi).
The flow factor - Kv - is also in common use, but express the capacity in SI-units.
The flow coefficient - Cv - required for a specific application can be estimated by using specific formulas for the different fluids or gases. With the estimated Cv value - the correct valve can be selected from the manufacturers catalogues.
For liquids the flow coefficient - Cv - expresses the flow capacity in gallons per minute (GPM) of 60oF water with a pressure drop of 1 psi (lb/in2).
Cv = q (SG / dp)1/2 (1)
q = water flow (US gallons per minute)
SG = specific gravity (1 for water)
dp = pressure drop (psi)
or alternatively in SI units:
Cv = 11.7 q (SG / dp)1/2 (1b)
q = water flow (m3/h)
dp = pressure drop (kPa)
Cv = w / (500 (dp SG)1/2) (1c)
w = water flow (lb/h)
dp = pressure drop (psia)
Cv = 5.32 w / (500 (dp SG)1/2) (1d)
w = water flow (kg/h)
The flow coefficient of a control valve which in the full open position passes 25 gallons per minute of water with a one pound per square inch pressure drop can be calculated as:
Cv = 25 (gpm) (1 / 1(psi))1/2
= 25
Since steam and gases are compressible fluids, the formula must be altered to accommodate changes in the density.
At choked flow the critical pressure drop the outlet pressure - po - from the control valve is less than 58% of the inlet pressure - pi. The flow coefficient can be expressed as:
Cv = m / 1.61 pi (2)
m = steam flow (lb/h)
pi = inlet steam absolute pressure (psia)
po = outlet steam absolute pressure (psia)
For non critical pressure drop the outlet pressure - po - from the control valve is greater than 58% of the inlet pressure - pi. The flow coefficient can be expressed as:
Cv = m / (2.1 ( (pi - po) po )1/2) (2b)
The flow coefficient for superheated steam should be multiplied with a correction factor:
Cv = Cv_saturated (1 + 0.00065 dt) (3)
dt = steam temperature above saturation temperature at the actual pressure (oF)
The flow coefficient for steam superheated with 50oF can be calculated as:
Cv = Cv_saturated (1 + 0.00065 (50oF) =1,0325 Cv_saturated
Saturated wet steam includes non evaporated water particles reducing the "steam quality" and very wet saturated steam should be multiplied with a correction factor:
Cv = Cv_saturated ζ1/2 (4)
ζ = dryness fraction
For steam with moisture content 5% the dryness fraction can be calculated as:
ζ = ws / (ww + ws) = 0.95 / (0.95 + 0.05) = 0.95
ww = mass of water
ws = mass of steam
The flow coefficient can be calculated as:
Cv = Cv_saturated (0.95)1/2 = 0,97 Cv_saturated
For critical pressure drop the outlet pressure - po - from the control valve is less than 53% of the inlet pressure - pi. The flow coefficient can be expressed as:
Cv = q [SG (T + 460)]1/2/ 660 pi (5)
q = free gas per hour, standard cubic feet per hour (Cu.ft/h)
SG = specific gravity of flowing gas gas relative to air at 14.7 psia and 60oF
T = flowing air or gas temperature (oF)
pi = inlet gas absolute pressure (psia)
For non critical pressure drop the outlet pressure - po - from the control valve is greater than 53% of the inlet pressure - pi. The flow coefficient can be expressed as:
Cv = q [SG (T + 460)]1/2/ [1360 (dp po)1/2] (5b)
dp = (pi - po)
po = outlet gas absolute pressure (psia)