Engineering ToolBox > Circulating Force in Gravity Heating Systems
Differential pressure due to difference in density between hot and cold water is the circulating force in a self circulating heating system
A self circulation heating system operates by the force created by the density difference between the hot and cold fluid.
gravity heating system
Gravity Head
The head available forcing circulation through a radiator in a gravity system is proportional to the elevation - he - of the radiator or heating element above the boiler, and the temperature difference between the flow and return pipes.
The head available for circulation can be expressed as:
hl = hr ( ρr - ρf ) / [( ρr + ρf ) / 2] (1)
hl = head available for circulation (m, ft)
hr = height of radiator or heating element above boiler (m, ft)
ρf = density of water in flow (hot) pipe (lb/ft3, kg/m3)
ρr = density of water in return (cold) pipe (lb/ft3, kg/m3)
The thermal expansion of water is 4.2% from 4 oC to 100 oC.
Converting Head to Pressure
Head can be converted to pressure units by the expression:
p = hl ρ g (2)
p = pressure (Pa, N/m2) - Other units?
ρ = density (kg/m3). Using hot or cold density have very little impact on this calculation.
g = gravitation 9.81 (m/s2)
Circulating Pressure - Flow and Return Temperature
The forcing pressures in self circulation system with operating temperatures between 50 to 95oC are indicated in the diagram and table below.
gravity heating pressure difference diagram
Circulating Pressure in Pa (N/m2) per m circulating elevation - he
Return Temperature
(oC)
Flow Temperature (oC)
40 50 60 70 80 90
90           0
80         0 64
70       0 59 123
60     0 54 113 177
50   0 48 101 161 225
40 0 41 89 143 203 267