Engineering ToolBox > Hazardous Areas Classification - North America
Electrical devices used in hazardous areas need to be certified for use according the requirements specified for the area.
In North America certification is provided by
The types of protection required depends on the risk involved in the area.
In general hazardous locations in North America are separated by classes, divisions, and groups to define the level of safety required for equipment installed in these locations.
The classes defines the general nature of hazardous material in the surrounding atmosphere.
| Class | Hazardous Material in Surrounding Atmosphere |
| Class I | Hazardous because flammable gases or vapors are present in the air in quantities sufficient to produce explosive or ignitable mixtures. |
| Class II | Hazardous because combustible or conductive dusts are present. |
| Class III | Hazardous because ignitable fibers or flying's are present, but not likely to be in suspension in sufficient quantities to produce ignitable mixtures. (Group classifications are not applied to this class.) |
The division defines the probability of hazardous material being present in an ignitable concentration in the surrounding atmosphere.
| Division | Presence of Hazardous Material |
| Division 1 | The substance referred to by class is present during normal conditions. |
| Division 2 | The substance referred to by class is present only in abnormal conditions, such as a container failure or system breakdown. |
The group defines the hazardous material in the surrounding atmosphere.
| Group | Hazardous Material in Surrounding Atmosphere |
| Group A | Acetylene |
| Group B | Hydrogen, fuel and combustible process gases containing more than 30% hydrogen by volume or gases of equivalent hazard such as butadiene, ethylene, oxide, propylene oxide and acrolein. |
| Group C | Ethyl and ethylene or gases of equivalent hazard. |
| Group D | Gasoline, acetone, ammonia, benzene, butane, cyclopropane, ethanol, hexane, methanol, methane, natural gas, naphtha, propane or gases of equivalent hazard. |
| Group E | Combustible metal dusts, including aluminum, magnesium and their commercial alloys or other combustible dusts whose particle size, abrasiveness and conductivity present similar hazards in connection with electrical equipment. |
| Group F | Carbonaceous dusts, coal black, charcoal, coal or coke dusts that have more than 8% total entrapped volatiles or dusts that have been sesitized by other material so they present an explosion hazard. |
| Group G | Flour dust, grain, wood, plastic and chemicals. |
The specific hazardous materials within each group and their automatic ignition temperatures can be found in Article 500 of the National Electrical Code and in NFPA 497.
Group A, B, C and D apply to class I locations. Group E, F and G apply to class II locations.
A mixture of hazardous gases and air may ignite in contact with a hot surface. The condition for ignition depends on several factors as surface area, temperature and concentration of gas.
Equipment approved receives a temperature code indicating the maximum surface temperature of the equipment.
| Temperature Code | Maximum Surface Temperature | |
| oF | oC | |
| T1 | 842 | 450 |
| T2 | 572 | 300 |
| T2A | 536 | 280 |
| T2B | 500 | 260 |
| T2C | 446 | 230 |
| T2D | 419 | 215 |
| T3 | 392 | 200 |
| T3A | 356 | 180 |
| T3B | 329 | 165 |
| T3C | 320 | 160 |
| T4 | 275 | 135 |
| T4A | 248 | 120 |
| T5 | 212 | 100 |
| T6 | 185 | 85 |
Equipment that not exceed a maximum surface temperature of 212 oF (104 oF ambient temperature) is not required to be marked with a temperature code (NEC).