Engineering ToolBox > Heat Emission from Radiators and Heating Panels
The heat emitted from a radiator or heating panel depends primarily on the temperature difference between the radiator and the surrounding air. The heat emission can be expressed as:
P = P50 * [ (ti - tr) / ln( (ti - ta) / (tr - ta) ) * 1 / 49.32 ]n (1)
where����������������
P = the emitted heat (W)
P50 = the emitted heat with an temperature difference 50oC (W). In general radiators are dimensioned1) for a middle temperature of 70oC and surrounding temperatures of 20oC (a difference of 50oC)
ti = water temperature inn (oC)
tr = water temperature out (oC)
ta = surrounding air temperature (oC)
n = constant describing the type of radiator (1.33 for standard panel radiators, 1.3 - 1.6 for convectors)
The heat emission from a radiator with nominal heat emission 1000 W (water temperature inn ti = 80oC, water temperature out tr = 60oC, surrounding air temperature ta = 20oC) with water temperature inn ti = 70oC and temperature out tr = 50oC can be calculated as
P = 1000 W * [ (70 - 50) / ln( (70 - 20) / (50 - 20) ) * 1 / 49.32 ]1.33
��� = 736 W
The calculator below can be used to calculate the actual heat emission and water flow from a radiator outside standard conditions - like increasing or decreasing the water inlet or outlet temperature or the surrounding room air temperature.
The calculator below can be used to calculate the water return temperature and the water volume flow through radiators based on actual heat emission and inlet water temperatures.
Oversized radiators are quite common since it is almost never possible to adapt standard radiators exactly to the required heat loss from a room. With the calculator below it is possible to study the consequence of out of standard heat emission when the radiator is oversized or when the outside temperature are higher than the design temperature, inlet or surrounding room temperature can be studied.����
When checking heat emission capacities of radiators, be aware that testing standards differs. Examples:
Testing the same radiator with BS EN442 will reduce the heat output with approximately 11% compared to BS 3528.�