Engineering ToolBox > Heat Loss from Buildings
Overall heat transfer loss from buildings - transmission, ventilation and infiltration
The overall heat loss from a building can be calculated as
H = Ht + Hv + Hi (1)
H = overall heat loss (W)
Ht = heat loss due to transmission through walls, windows, doors, floors and more (W)
Hv = heat loss caused by ventilation (W)
Hi = heat loss caused by infiltration (W)
1. Heat loss through Walls, Windows, Doors, Ceilings, Floors, etc.
The heat loss through walls, windows, doors, ceilings, floors etc. can be calculated as
Ht = A U (ti - to) (2)
Ht = transmission heat loss (W)
A = area of exposed surface (m2)
U = overall heat transmission coefficient (W/m2K)
ti = inside air temperature (oC)
to= outside air temperature (oC)
Heat loss through roofs should be added 15% extra because of radiation to space. (2) can be modified to:
H = 1.15 A U (ti - to) (2b)
For walls and floors against earth (2) should be modified with the earth temperature:
H = A U (ti - te) (2c)
te= earth temperature (oC)
Overall Heat Transmission Coefficient
The overall of heat transmission coefficient - U - can be calculated as
U = 1 / (1 / fi + x1 / k1 + x2 / k2+ x3 / k3 +..+ 1 / fo) (3)
fi = surface conductance for inside wall (W/m2K)
x = thickness of material (m)
k = thermal conductivity material (W/mK)
fo= surface conductance for outside wall (W/m2K)
The conductance of a building elements can be expressed as:
C = k / x (4)
C = conductance, heat flow through unit area in unit time (W/m2K)
The thermal resistivity of the building element can be expressed as:
R = x / k = 1 / C (5)
R = thermal resistivity (m2K/W)
Using (4) and (5), (3) may be modified to
1 / U = Ri + R1 + R2 + R3 + .. + Ro (6)
For walls and floors against earth (6) should be modified to
1 / U = Re + SR (6b)
2. Heat Loss caused by Ventilation
The heat loss due to ventilation without heat recovery can be expressed as:
Hv = cp ρ qv (ti - to) (7)
Hv = ventilation heat loss (W)
cp = specific heat capacity of air (J/kg/K)
ρ = density of air (kg/m3)
qv = air volume flow (m3/s)
to = outside air temperature (oC)
The heat loss due to ventilation with heat recovery can be expressed as:
Hv = (1 - β / 100) cp ρ qv (ti - to) (7)
β = heat recovery efficiency (%)
An heat recovery efficiency of approximately 50% is common for a normal cross flow heat exchanger. For a rotating heat exchanger the efficiency my exceed 80%.
3. Heat Loss caused by Infiltration
Due to leakages in the building construction, opening and closing of windows, etc. the air in the building shifts. As a rule of thumb the number of air shifts is often set to 0.5 per hour. The value is hard to predict and depend of several variables - wind speed, difference between outside and inside temperatures, the quality of the building construction etc.
The heat loss caused by infiltration can be calculated as
Hi = cp ρ n V (ti - to) (8)
Hi = heat loss infiltration (W)
n = number of air shifts, how many times the air is replaced in the room per second (1/s) (0.5 1/hr = 1.4 10-4 1/s as a rule of thumb)
V = volume of room (m3)