Engineering ToolBox > Heat Loss from Open Water Tanks
Due to evaporation - heat loss from open water tank as a swimming pools, may be considerable
The overall heat loss from an open water tank can be expressed as:
Q = Qevaporation fluid + Qradiation fluid + Qtransmission through walls (1)
The heat loss due to evaporation of water from a surface of an open tank is totally dominant at higher water temperatures. In general heat loss through insulated walls can be almost neglected. Major heat loss can be avoided by covering the surface.
Water Temperature (oF) Heat Loss from Liquid Surface
(Btu/ft2hr)
Heat Loss Through Tank Walls
(Btu/ft2hr)
Evaporation Loss Radiation Loss Total Bare Steel Uninsulated Insulated (inches)
1 2 3
90 80 50 130 50 12 5 4
100 160 70 230 70 15 8 6
110 240 90 330 90 19 10 7
120 360 110 470 110 23 12 9
130 480 135 615 135 27 14 10
140 660 160 820 160 31 16 12
150 860 180 1040 180 34 18 13
160 1100 210 1310 210 38 21 15
170 1380 235 1615 235 42 23 16
180 1740 260 2000 260 46 25 17
190 2160 290 2450 290 50 27 19
200 2680 320 3000 320 53 29 20
210 3240 360 3600 360 57 31 22
Heat loss are for open tanks in 60oF still ambient air.
heat loss from open tanks or swimmingpools chart