Engineering ToolBox > Heating Humid Air
Calculating enthalpy change and temperature rise when sensible heating moist and humid air
The process of sensible heating of air can be expressed in the Mollier diagram as:
psychrometrics heating air
Heating of air moves the air condition from A to B along a constant specific humidity - x - line. The supplied heat - dH - can be read in the diagram as shown.
The heating process of air expressed can also be expressed in the psychrometric chart as:
pshycrometric chart
Note! When heating air the specific moisture remains constant and the relative humidity decreases.
Calculating Enthalpy
The enthalpy of moist air can be expressed as:
h = cpa t + x [cpw t + hwe] (1)
h = specific enthalpy of moist air (kJ/kg)
cpa = 1.01 - specific heat capacity of air at constant pressure (kJ/kg.oC, kWs/kg.K)
t = air temperature (oC)
x = humidity ratio (kg/kg)
cpw = 1.84 - specific heat capacity of water vapor at constant pressure (kJ/kg.oC, kWs/kg.K)
hwe = 2,502 - evaporation heat of water at 0oC (kJ/kg)
(1) can be modified as:
h = 1.01 (kJ/kg.oC) t + x [1.84 (kJ/kg.oC) t + 2,502 (kJ/kg)] (1b)
The Enthalpy Difference
The enthalpy difference when heating air without changing moisture content can be expressed as:
dhA-B = cpa tB + x [cpw tB + hwe] - cpa tA + x [cpw tA + hwe]
= cpa(tB - tA) + x cpw (tB - tA) (2)
Example - Enthalpy Difference Heating Air
The specific humidity of air at 25oC and relative moisture 50% is 0.0115 kg/kg - check the Mollier diagram. The change in enthalpy when heating the air to 35oC can be calculated as:
dhA-B = (1.01 kJ/kg.oC)(35oC - 25oC) + (0.0115 kg/kg) (1.84 kJ/kg.oC) (35oC - 25oC)
= 10.1 kJ/kg + 0.2 kJ/kg
= 10.3 kJ/kg
Note! The contribution from the water vapor is relatively small and for practical purposes it may often be neglected. (2) can then be modified to:
dhA-B = cpa( tB - tA) (2b)
Increase in Temperature when Heating Air
If heat is added to humid air the increase air temperature can be calculated by modifying (2b) [(2) to be more exact]:
tB - tA = dhA-B / cpa (2b)
Example - Heating Air and Temperature Rise
If 10.1 kJ is added to 1 kg air, the temperature rise can be calculated as:
tB - tA = (10.1 kJ/kg) / (1.01 kJ/kg.oC)
= 10oC
Heat Flow in a Heating Coil
The total heat flow rate through a heating coil can be calculated as:
q = m (hB - hA) (3)
q = heat flow rate (kJ/s, kW)
m = mass flow rate of air (kg/s)
The total heat flow can also be expressed as:
qs = v ρ (hB - hA) (3a)
v = volume flow (m3/s)
ρ = density of air (kg/m3)
Note! The density vary with temperature. At 0oC the density is 1.293 kg/m3. At 80oC the density is 1.0 kg/m3.
It's common to express the sensible heat flow rate as:
q = m cpa (tB - tA) (3b)
or alternatively:
q = v ρ cpa (tB - tA) (3c)
Heating Coil Effectiveness
For a limited heating coil surface the average surface temperature will always be higher than the outlet air temperature. The effectiveness of a heating coil can be expressed as:
μ = (tB - tA) / (tHC - tA) (4)
μ = heating coil effectiveness
tHC = mean surface temperature of the heating coil (oC)
1 m3/s of air at 15oC and relative humidity 60% (A) is heated to 30oC (B). The surface temperature of the heating coil is 80oC. The density of air at 20oC is 1.205 kg/m3.
From the Mollier diagram the enthalpy in (A) is 31 kJ/kg and in (B) 46 kJ/kg.
The heating coil effectiveness can be calculated as:
μ = (30oC - 15oC) / (80oC - 15oC)
= 0.23
The heat flow can be calculated as:
q = (1 m3/s) (1.205 kg/m3) ((46 kJ/kg) - (31 kJ/kg))
= 18 (kJ/s, kW)
As an alternative, as one of the most common methods:
q = (1 m3/s) (1.205 kg/m3) (1.01 kJ/kg.oC) (30oC - 15oC)
= 18.3 (kJ/s, kW)
Note! Due to inaccuracy when working diagrams there is a small difference between the total heat flow and the sum of the latent and sensible heat. This inaccuracy is in general within acceptable limits.