Engineering ToolBox > Friction or Major Resistance in Condensate Lines - Imperial Units
A table for estimating capacity of condensate piping lines
The table below can be used for the running load. As a common rule of thumb, if the start up condition is unknown, the running load should be doubled when sizing condensate pipes.
Avoid friction resistance above 10 inches Water gauge - Wg - per 100 ft of pipe.
Weight of Condensate (lb/h) Frictional Resistance - Major loss (inches Wg per 100 ft of pipe)
Pipe Size (inch) 1 5 7 10 14 16 20
1/2 100 240 290 350 430 460 520
3/4 230 560 680 820 990 1000 1200
1 440 1070 1200 1550 1800 2000 2260
1 1/4 950 2300 2700 3300 4000 4300 4800
1 1/2 1400 3500 4200 5500 6100 6600 7100
2 2800 6800 8100 9900 11800 12700 14200
2 1/2 5700 13800 16500 20000 23900 25700 28900
3 9000 21500 25800 31000 37000 39800 44700
4 18600 44000 52000 63400 75500 81000 90900
Example - Sizing a Condensate Pipe
For steam distribution system with a running load of 2000 lb/h - the startup condensate load should be set to 4000 lb/h.
A reference to the 10 inch Wg column gives the 1 1/2 inch pipe as the most suitable.