Engineering ToolBox > Safety Valves in High Pressure Steam Systems
Sizing safety valves after boiler output power in high pressure systems (kW and Btu/hr)
The main purpose of the safety valve is to prevent the pressure in the systems to exceed certification pressure. Above certification pressure, no one can guaranty the systems safety - and especially for a steam system with very hot gas with huge amount of latent heat, the consequences can be dramatically.
The size of the safety valve depends primarily on the maximum boiler output and the operation pressure of the system. The safety valve shall as minimum have the evacuation capacity of all the vapor the boiler can produce running at full power at the working (or certification) pressure.
The tables below can be used for selecting typical safety valves in high pressure systems. Before final design, always consult manufacturing documentation.
Steam Pressure 1000 kPa (10 bar) and 150 psi
Pipe Size Capacity Maximum Boiler Output
in DN (mm) kg/h lb/h kW Btu/h
1/2 15 220 498 122 426 786
3/4 20 472 1 070 262 916 990
1 25 827 1 875 459 1 606 875
1 1/4 32 1 421 3 222 789 2 761 254
1 1/2 40 2 058 4 668 1 143 4 000 476
2 50 3 065 6 954 1 702 5 959 578
2 1/2 65 5 144 11 670 2 856 10 001 190
3 80 7 108 16 124 3 947 13 818 268
4 100 13 694 31 067 7 604 26 624 419
Note! The table above is based on high pressure steam of 1000 kPa (10 bar) or 150 psi in imperial units. Latent heat of saturated steam is 1999 kJ/kg (857 Btu/lb).
Steam Pressure 700 kPa (7 bar) and 100 psi
1/2 15 159 346 90 304 480
3/4 20 342 743 194 653 840
1 25 599 1 302 340 1 145 760
1 1/4 32 1 030 2 238 585 1 969 440
1 1/2 40 1 792 3 242 1 018 2 852 960
2 50 2 222 4 827 1 263 4 247 760
2 1/2 65 3 730 8 101 2 120 7 128 880
3 80 5 153 11 193 2 929 9 849 840
4 100 9 929 21 566 5 643 18 978 080
Note! The table above is based on high pressure steam of 700 kPa (7 bar) or 100 psi in imperial units. Latent heat of saturated steam is 2046 kJ/kg (880 Btu/lb).
Steam Pressure 300 kPa (3 bar) and 50 psi
1/2 15 79 193 47 176 016
3/4 20 169 414 100 377 568
1 25 296 726 175 662 112
1 1/4 32 509 1 248 302 1 138 176
1 1/2 40 737 1 807 437 1 647 984
2 50 1 099 2 695 651 2 457 840
2 1/2 65 1 844 4 522 1 093 4 124 064
3 80 2 547 6 248 1 509 5 698 176
4 100 4 907 12 038 2 907 10 978 656
Note! The table above is based on high pressure steam of 300 kPa (3 bar) or 50 psi in imperial units. Latent heat of saturated steam is 2133 kJ/kg (912 Btu/lb).
1 N/m2 = 1 Pa = 1.4504 x 10-4 lb/in2 (psi) = 1x10-5 bar