Engineering ToolBox > Classification of Ventilation Dampers
Dampers in ventilation systems may be classified according function, construction or leakage class
ventilation damper
Classification by Function
Dampers may be classified according their functional tasks in the ventilation system:
Classification by Construction
Classification by Leakage Class
The leakage class determines the acceptable air leakage through the damper with a 100 Pa pressure difference. The leakage classes are:
The air flow rates through the dampers at 100 Pa are in general available from the manufacturers catalogues.
Function Class
1 2 3
Adjustment x
Closing, running x
Closing, smoke x
Closing, fire x
Overpressure x
Modulation x
Calculating Leakage Air Flow Rate through a Closed Damper
The leakage air flow through a closed damper can be calculated if the the difference pressure through the damper and the leakage air flow rate at 100 Pa (manufacturer data) through the damper is known:
ql = q100 (dpl / 100)1/2 (1)
ql = actual volume flow per m2 valve area (m2/s m2)
q100 = volume flow at 100 Pa per m2 valve area (m2/s m2)
dpl = actual pressure drop through the valve (Pa)