Engineering ToolBox > Sizing Water Supply Lines
Due to intermittent use of the fixtures in a water supply system it can be difficult to predict and size the supply and service lines. The fixtures total theoretical demand should always be compensated with a statistic more expected demand.
With the Water Supply Fixture Units (WSFU) system defined by the Uniform Plumbing Code (UPC) there are tables available where the total demand calculated by adding each units "Water Supply Fixture Units" (WFSU) are compensated to an expected demand.
The tables below can be used to size building supply and branch lines and meter and service lines.
| Maximum Water Supply Fixture Units (WFSU) | |||||||
| Meter and street service lines (inches) | Building supply and branch lines (inches) | Length of pipe (feet) | |||||
| 40 | 60 | 80 | 100 | 150 | 200 | ||
| 3/4 | 1/2 | 6 | 5 | 4 | 3 | 2 | 1 |
| 3/4 | 3/4 | 16 | 16 | 14 | 12 | 9 | 6 |
| 3/4 | 1 | 29 | 25 | 23 | 21 | 17 | 15 |
| 1 | 1 | 36 | 31 | 27 | 25 | 20 | 17 |
| 1 | 1 1/4 | 54 | 47 | 42 | 38 | 32 | 28 |
| 3/4 | 1/2 | 7 | 7 | 6 | 5 | 4 | 3 |
| 3/4 | 3/4 | 20 | 20 | 19 | 17 | 14 | 11 |
| 3/4 | 1 | 39 | 39 | 36 | 33 | 28 | 23 |
| 1 | 1 | 39 | 39 | 39 | 36 | 30 | 25 |
| 1 | 1 1/4 | 78 | 78 | 76 | 67 | 52 | 44 |
| 3/4 | 1/2 | 7 | 7 | 7 | 6 | 5 | 4 |
| 3/4 | 3/4 | 20 | 20 | 20 | 20 | 17 | 13 |
| 3/4 | 1 | 39 | 39 | 39 | 39 | 35 | 30 |
| 1 | 1 | 39 | 39 | 39 | 39 | 38 | 32 |
| 1 | 1 1/4 | 78 | 78 | 78 | 78 | 74 | 62 |
The tables can be used for pipe lines but for special equipment like manifolds etc. a table or formula converting the WSFU to water flow should be used for proper sizing.